Danfos db35f 3 flashes error

Started by elias, December 17 2022, 15:34

Previous topic - Next topic

elias

Hi to all ,
I decided to service the fridge by changing filter and adding /cleaning coolant ...
The technician came all done , and after 30min . The fridge stopped cooling . Switched it off for some seconds and after turning it on again the compressor don't start up and I get 3 flashes . If I let it rest more time it starts cooling but only for some minutes ...
Any ideas ? Overcharged ? His torch burned something ? He is coming again in some days

elias

Also now I noticed that something violent sounds when tries to start up

Yngmar

3 flashes means:

QuoteMotor start error
(The rotor is blocked or the differential pres-
sure in the refrigeration system is too high
(>5 bar)).

Since it recovers after sitting for a while, I'd say it's got a blockage somewhere, so your worker probably lost some debris in the pipe.

So in summary, you had a working fridge, did some unnecessary "servicing" and now you have a broken fridge?  >:D
formerly Songbird - Bavaria 40 Ocean (2001) -- now gone farming

elias

I had this feeling from the first place but I said what the heck , is at least 10 years as far as I know unserviced...
Here know we start with issues , cause for sure the compressor stressed and that might decreased its life span maybe ?

tiger79

Quote from: elias on December 17 2022, 18:46
I had this feeling from the first place but I said what the heck , is at least 10 years as far as I know unserviced...


10 years is nothing, these things can run for ages before repairs are needed.

elias

I also calculated that it starts with 3 amps and the hissing sound on the evaporator and then after some time the hissing sounds stops and the amps drop to 2 and eventually stops

elias

Hi ,
Finally was partially blocked cap tube due to moisture and dirt as the tech guy confessed ...